- Esp field rating during unit lightup
- Esp field rating when hopper empty.
Durgendra Tripathi Changed status to publish
In Electrostatic Precipitators (ESP) during unit light-up and hopper empty condition, the field rating (kV & mA) is set carefully to avoid damage and false alarms. The logic is as follows:
1. Unit Light-up Condition
- At boiler light-up, flue gas temperature is low and dust load is negligible.
- ESP should not be operated at full rating, otherwise back corona and spark rate will increase.
- Typical practice:
- Keep ESP fields in “Auto” but with reduced TR setpoints (around 20–25 kV or ~30% of design rating).
- Spark rate limit lowered (to ~20 sparks/minute) for protection.
- As the load increases and flue gas stabilizes, gradually raise to normal operating level (40–50 kV as per design).
2. Hopper Empty Condition
- Hopper emptying causes rapping and sudden dust re-entrainment.
- If ESP fields remain at full rating, it may lead to excessive sparking and load tripping.
- Typical practice:
- Put the concerned fields in “Voltage Limiting” mode or reduce to ~60–70% of rated kV before rapping.
- Once dust settles, return gradually to Auto mode with full kV/mA rating.
- Some stations even bypass fields for a few minutes during heavy rapping.
General Guideline
- Always follow OEM/plant-specific SOPs because design ratings vary (some ESPs operate at 50–60 kV, others up to 70 kV).
- During light-up/low load → keep ESP in safe mode with reduced rating.
- During hopper emptying/rapping → derate fields temporarily.
- Once stable → switch back to auto optimization (high efficiency mode).
Admin Changed status to publish